PMDX Forum
General Category => Parallel Port breakout boards, motherboards, and dedicated accessories => Topic started by: KG7AMV on July 20, 2015, 12:52:20 AM
-
I cannot get the 107 to talk to the VFD. Test Mode when it exits it does give it some com when A001 is set to control terminal and A002 is set to key pad and switched to run. When Hooked to a POT it works as it should just not with the PMDX-107. PMDX-126 W/ESS
VFD is a HITACHI WJ200-022SF Settings. See Quick Reference Page 50: http://www.hitachi-america.us/supportingdocs/forbus/inverters/Support/NT3251X.pdf
A001 set at 01 Even Tried 00 (A001: 01 Control Terminal, 00 Pot Control On Ext Operator
A002 Set to 01 Control Terminal
PLC is jumped to L on upper row "Source Logic" (Page 27)
Connecting the 107 to the VFD
Rev/Dir to Terminal 2 on VFD
Fwd/Run to Terminal 1 on VFD
COM ? P24 on VFD
Aref to H on VFD
Aout to O on VFD
Agnd - L on lower row on VFD
Dip 6 On For RatioMetric (Tried it Both Ways On and off).
Am I doing something Wrong In the hookup or settings?
-
Got it! Was a bad wire.
-
Seems it will only run clockwise. M3 & M4 do nothing if I go to pulleys and select reverse it will run reverse counter clockwise.
I followed the AN002 instructions.
Wonder what setting I am missing?
-
Thanks Steve for all the help today.
Corrupted Mach 3 Config File was the issue.
-
It's always something other than what you figured it would be.... 8-)