General Category => SmartBOB controllers and dedicated accessories => Topic started by: broered on April 23, 2016, 12:38:03 PM
-
Gecko 203V's have a disable terminal. Their manual says that you can force winding currents to ZERO by connecting this terminal to the Step/Direction controller's +5V.
I'd like to tie all 4 of the 203V's disable terminals to a single switch, then to 5V, somewhere on the PMDX-424.
(1) can I tie all 4 of the 203V's disable terminals together without causing problems?
(2) what's the best place, on the PMDX-424, to get the 5V from?
thanks
Dave
-
Yes, you can tie the "Disable" input on all of the G203V drivers together. The 5V to drive the "Disable" input can come from the "L+5V" terminal on J12 or J13. These connector shares the same ground as the step/direction outputs.**
** NOTE: Well, the "ground" that can appear on the step/dir "com" terminal is not actually ground, but ground through a buffer IC. So when the step/dir common is set to "ground", it may actually be a 1/10th or two above the "Lgnd" on J12 or J13. But that is OK as far as the G203V is concerned.
Bob
-