Messages - jbolt

Pages: [1]
1
I finally figured it out. The VFD has an on-board potentiometer that was interfering with the output of the pmdx-106. There is a jumper in the VFD for on-board or external input. After making that change I had to change the wiring from the 106 to the VFD:

J6 NO --> FOR (VFD PD044 = 02)
J6 COM --> DCM

J8 NO --> REV (VFD PD0045 = 03)
J8 COM --> DCM

J2 LOW --> AGM
J2 SET --> VI

After making those changes I was able to run the calibration on the PMDX-106

2
I checked the  pmdx-106, output voltage on J2. On first press of the test button I get 7.67v and the vfd goes to 100%. On the second press the voltage drops to 2.046v and the vfd stays at 100%. VFD will not go to 30%. In Mach3 I can turn the spindle on in forward or reverse with M3 & M4 but I cannot set the speed.

Settings:

PMDX-122 Settings:

J5 Pin 11 --> X Home/Limit
J5 Pin 12 --> Y Home/Limit
J5 Pin 13 --> Z Home/Limit

J8 +5v --> (From PC Power Supply Lead)
J8 Pin 14 --> PMDX-106 J9 DIR IN
J8 Pin 16 --> PMDX-106 J3 PWM IN
J8 Pin 17 --> PMDX-106 J3 CP-OK
J8 GND --> (From PC Power Supply Lead)

JP1 +5v/Pin 2-9
JP2 Pin 2-9/OK
JP3 Output Enable/CP-OK
JP4 Pin 17/OK
JP5 DIR/OUT

=====================================================

PMDX-106 Settings:
J3 CP-OK --> Pin 17
J3 PWM IN --> Pin 16

J9 DIR IN --> Pin 14

J2 LOW --> VFD (VI) Analog Voltage Frequency Reference Input (0-+10v corresponding to the highest operating frequency)
J2 SET --> VFD (AGM) Common terminal of analog and control signals

J4 +5v --> (From PC Power Supply Lead)
J4 GND --> (From PC Power Supply Lead)

(See attached image of J6 & J8 wiring)
J6 NO --> VFD (D1, FOR)
J6 COM --> VFD (DCM) Common terminal of digital and control signals
J6 NC --> VFD (D2, REV)

J8 NO --> VFD (D1, FOR)
J8 COM --> VFD (DCM) Common terminal of digital and control signals

JP1 Loc/Ref
JP2 0-10v

Dip Switches (all off)

=====================================================

VFD: Huanyang HY01D511B
3PHAC110 +- 20% 50Hz +- 5Hz
3PH 0~110AC 1.5KW 13A 0.50 - 400.00Hz

VFD Parameter set:

PD001 = 1 (external control)
PD002 = 1 (external control)
PD003 = 400 (Main Frequency)
PD004 = 400 (Base Frequency)
PD005 = 400 (Max Operating Frequency)
PD006 = 2.5 (Intermediate Frequency)
PD007 = 20.00 (Min Frequency)
PD008 =110 (Max Voltage)
PD009 = 14 (Intermediate Voltage)
PD010 = 7 (Min Voltage)
PD011 = 120 (Frequency Lower Limit)
PD013 = 1 (Vendor Recommended Setting)
PD014 = 5 (Accelleration time in sec)
PD015 = 5 (Deceleration time in sec)
PD027 = 0.50 (Starting Frequency)
PD028 = 0.50 (Stopping Frequency)
PD070 = 1 (Set Control Voltage to 0-5v) (setting to " = 0", 0-10v, causes the spindle to run at 50%)
PD072 = 400 (Higher Analog Frequency)
PD073 = 120 (Lower Analog Frequency)
PD141 = 110 (Rated Motor Voltage) (From Motor Label)
PD142 = 5.0 (Rated Motor Current) (From Motor Label)
PD143 = 2 (Motor Poles)
PD144 = 3000 (Rated Motor Revolutions)
PD0176 = 60hz (Inverter Frequency Standard)

=====================================================

Mach3 Settings:
See attached XML file

=====================================================

Motion Controller:

UC100

3
I have changed the BOB to a PMDX-122 and with some help from another forum I now have the spindle running fwd and rev from Mach3. In test mode on the 106 I cannot get the spindle to reduce speed to 30%, it stays at 100%. I am also unable to change speed in Mach3. I suspect it is a VFD setting but I believe I have everything set correctly. I did find that PD070 was set to 0-5v analog input. I cahnged it to 0-10v but with this setting the spindle only goes to 50% (200hz) and I still cannot change speed. The 106 J1 & J2 jumpers are set for 0-10vdc.

Ant thoughts on what needs to be changed would be appreciated.

Jay

4
My second question is how the PDMX-106 is wired to the VFD.

It is a Huangyang 1.5kw vfd.
The VFD control inputs are:

FWD  =    forward rum
REV  =    reverse run
DCM  =   common terminal for digital inputs
VI      =      0-10v analog input
ACM  =      analog input ground

I understand from the manual that VI = Connector J2 SET and ACM = J2 LOW. jumper on ref-to-pot/local

How does the PMDX-106 hookup to the VFD FWD, REV & DCM terminals? J6 & J8? and if so to which terminals. nc, com or no?  or???

Jay

5
[Amended] I have changed the subject to reflect the current configuration and added information on the current setup and problems below.

Jay

6
I got it. I'm a bit thick in the head sometimes. I set PD072 to 105hz and re-ran the Calibration. Tuned the spindle to 6000 rpm and all is working perfect.

Thank you again for your time!

Best Regards,

Jay

7
Steve,

A bit of a breakthrough. I went through the VFD settings and found PD072 -" Higher Analog Frequency" to have been  factory set at 400hz. I changed this to 105hz and it slowed everything down too much so I put it at 200hz and now I am getting close to the correct values. With the trim pot at full CCW at 30% I now get 34hz which is a little higher than I should have. I could possibly tune the PD072 value but I'm not sure what this setting is for?

I believe we are out of the realm of PMDX issues so thank you for your help.

Jay

8
Steve, I freally appreciate your feedback.

Running the CAL test with the pot set full CCW I get no increase in spindle speed. Always 100% (105hz) no matter where the pot is. At 30% with the pot at full CCW the VFD drops to 67hz. With the pot at a half tun the 30% speed is 94hz.

So it sounds like it is a VFD setting?

Thanks,
Jay

9
Steve,

That made some progress but now (on pulley 1) if I enter s3000 or above I get 100% (6000 rpm). S1500 gives me appox 3000 rpm. So it appears to be doubling somewhere. I'm wondering if there is another VFD setting that needs to be set?

Thanks,
Jay

10
These are my setting if it is of any help.

PMDX-126 BOB, PMDX-107 Motor Control, ESS Motion Controller.

MOTOR, 220v, 2hp, 3ph, 1725rpm, inverter duty, class F

VFD = Huanyang HY02D223B Settings

pd001 = 1, run command = external terminals
PD002 = 1, operating frequency source = external terminals
pd003 = 60.00, main frequency
pdoo4 = 60.00, base frequency
pd005 = 120.00, max frequency
pd008 = 220, max voltage
pd141 = 220, rated motor voltage
pd142 = 8.0, rated motor current
pd143 = 4, motor pole number
pd144 = 1725, rated motor revolution
pd176 = 60.00, inverter frequency standard


ESS Settings

SPINDLE
PWM, base hz 25


Mach3 Settings

RELAY CONTROL, disabled

MOTOR CONTROL
Use Spindle Motor Output
PWM Control
PWM Base Freq = 25
Minimum PWM 5%

SPINDLE MOTOR TUNING
Steps per = 1000
Velocity = 60
Acceleration = 5000

PULLEY SELECTION
Pulley 1, Min Speed = 300, Max Speed = 6000, Ratio = 2 (4" motor pulley, 2" spindle pulley)
Pulley 2, Min Speed = 75, Max Speed = 1500, Ratio = 0.5 (2" motor pulley, 4" spindle pulley)

Thanks
Jay

11
Found one problem. I did not have one of the VFD parameters set for the proper frequency input.

Now when I run the test I get 100% (105hz) on the first button push and approximately 60%(67hz) on the second button push. It still does not go to 30%.

In mach3 I have the pulley setup for Max rpm of 6000 (105hz) Min rpm of 300 (5%) and a pulley ratio of 2 (4" motor pulley/ 2" spindle pulley). I don't know what the reverse box is for but I have tried at ratio od 0.5, 1 and 2 with the reverse box checked and un-checked with no difference. It always goes to 100% on an M command regardless of the S command setting. I can use the override to slow or speed up the spindle.

12
Also when I run the test mode the VFD will not go to 30% on the second test button push.

Jay

13
Stave, thank you for the clarification on the relays. The manual had me thinking K1 and K2 were disabled because of the 107.

I have the spindle turning on/off with Mach3 but I cannot set the speed. The spindle always goes to full speed regardless of the "S" command. Mach3 thinks it is going to the correct speed but it is always 100%.

I followed the AN002 so I'm not sure where I have gone wrong?

Jay

14
Steve,

Thank you for confirming the control wiring.

I am still unsure of the settings for JP1 & JP2 and the config switches 7 & 8 on the pmdx-126.

Additionally, with 4 axis and the 107 all the output pins from PP#1 are used. To control two solid state relays for coolant and mist do I use A, B, C or D on J5 on PP#2? 

Jay

15
I have my PMDX-126 and ESS working with no problems. I am now converting the gear head mill to a variable speed belt drive. I need some help verifying if I have the correct connections from the PMDX-107 to the VFD, how the jumpers on the PMDX-126 need to be configured and what settings on the PMDX-126 need to be made to control two solid state relays for coolant and mist.

I have the VFD running the motor in manual mode so that is all okay. The VFD is a Huanyang HY02D223B.

These are the settings I think are correct.

PMDX-107 ---> VFD
Pin 6 - Rev/Dir ---->       REV (reverse run)
Pin 5 - Fwd/Run ---->    FOR (forward run)
Pin 4 - COM (common terminal for relays, pins 5 & 6) ----> DCM (common terminal of digital and control signals)
Pin 3 - Aref (not used)
Pin 2 - Aout (spindle speed analog control voltage) ----> VI (analog voltage frequency reference input)
Pin 1 - Agnd (VSD ground reference) ----> ACM (common terminal of analog and control signals)

PMDX-107  Config settings (dip switches)
Config 1 = Off (Normal Mode)
Config 2 = Off (Normal Mode)
Config 3 = Off (relays operate as for and reverse control signals)
Config 4 = Off (charge pump signal required)
Slow = Off (fast PWM filter response) (may need to be changed to slow if VFD cannot keep up)
5v/10v = Off (10v reference)
 
PMDX-126 Settings
Config 1 = Open
Config 2 = Closed
Config 3 = Closed
Config 4 = Closed
Config 5 = Closed
Config 6 = Closed
Config 7 = ???
Config 8 = ???

Pages: [1]