This one of the most complex VFDs that I have ever seen. The manual is
over 500 pages! Here is a link to the manual that I found:
http://download.lenze.com/TD/i550%20Cabinet%200,25-45kW%20(Firmware%2002%2001%2001%2000)__v4-0__EN.pdfThe best information that I found was on page 381.
Based on that diagram, your connections would be:
PMDX-107 VFD
Agnd X3-GND
Aout X3-AI1
Aref X3-10V
COM X3-24V
Fwd/Run X3-DI2
Rev/Dir X3-DI3
jumper X3-24V to X3-DI1
set parameters as per the chart below the wiring diagram on page 381
set the PMDX-107 as below:
Config1 - off
Config2 - off
Config3 - off (standard independent run FWD and run REV
Config4 - as desired, off for require Charge Pump, or on to ignore
Config5 - off (fast response mode, VFD will limit as needed)
Config6 - off (10 volt mode)
I do not know what the default settings of other parameters in
this VFD are, so if you are running a 24,000 RPM, 400 Hz spindle
you may need assistance from Lenze with setting the parameters.