Thank you for the information I have everything talking except the relay I bought to control the router not sure how to wire that up any advice would great thank you MD20 120 is the relay
Presuming that you want to use this contactor to control AC power into the router (wood router??) and that you are not trying to control the direction of the router:
(1) Connect the "hot" lead of the 120VAC into the "Fwd/Run" terminal on the PMDX-107
(2) Connect to "COM" terminal on the PMDX-107 terminal "0" (or "1") on the MD20 contactor
(3) Connect the "1" terminal on the MD20 back to the 120VAC neutral that pairs with the "hot" lead in step (1).
(4) Connect the "hot" lead of the 120VAC (or 240VAC depending on your motor) to MD20 terminal "2"
(5) Connect MD20 terminal "4" to the AC "hot" wire into your router motor
(6) Connect the "neutral" lead of the 120/240VAC power to MD20 terminal "6"
(7) Connect MD20 terminal "8" to the AC" neutral" wire into your router motor
(8) If you router motor has an earth ground wire, connect that to your system's earth/safety ground.
(9) On the PMDX-107, set DIP Switch "Config3" to "On" so that the "Fwd/Run" terminal acts as the "Run" signal.
Steps (1) to (3) and (9) set the PMDX-107 to energize the contactor coil when the spindle is running. The other steps route both the 'hot" and "neutral" AC power lines through the contactor contacts.
Bob