Author Topic: PMDX-107 Test mode runs Rev  (Read 7336 times)

Techsavvy34

  • Posts: 23
    • View Profile
PMDX-107 Test mode runs Rev
« on: September 29, 2015, 03:42:10 PM »
When I use test mode on the pmdx-107 my spindle runs in reverse.  I have it wired as Run/Dir mode.  When I issue a m3 command it runs forward.  Is this normal for this mode or is a setting wrong in my commander sk vfd?

Steve Stallings

  • Administrator
  • Posts: 530
  • www.PMDX.com/Images/Avatar120.jpg
    • View Profile
Re: PMDX-107 Test mode runs Rev
« Reply #1 on: September 29, 2015, 05:17:38 PM »
Without knowing what your spindle driver is, I cannot say for sure.

What matters is getting results consistent with your expectations. Otherwise
it makes little difference what the test mode does.

If your spindle runs in reverse in test mode and you have a 3 phase  induction motor,
you can swap two of the phase wires to make the motor rotation match the test mode.
Then go into your pin configuration in the software and invert the direction signal.

If your spindle is a DC motor or a BLDC motor, then you could look to see if
the spindle driver offers an option to reconfigure the action of the direction
input signal.
Steve Stallings
www.PMDX.com

Bob at PMDX

  • Administrator
  • Posts: 368
    • View Profile
    • PMDX
Re: PMDX-107 Test mode runs Rev
« Reply #2 on: September 29, 2015, 05:30:44 PM »
Oops - Steve answered as I was typing this.  Lets see if I can offer anything in addition to his answer.

The short answer is that if it works properly for M3 and M4 commands, then it is OK.  Just know that the spindle will run backwards when using the PMDX-107 test mode (which you should only need to do when setting up your machine).

If you want the PMDX-107 test mode and your M3 commands to both run the spindle in the same direction, then keep reading...

The PMDX-107 has several LEDs on it, including one for each of the solid-state relay outputs (in your case, one for "Run" and one for "Dir").  These are located just below the screw terminals for these two signals.  When you use the PMDX-107's test mode, the "Run" LED should light up and the "Dir" LED should remain off.

When you issue an "M3" command, does the "Dir" LED on the PMDX-107 light up or does it remain off?  How about an "M4" command?  I'm betting that the "M3" command causes the "Dir" LED to light up.

Since you are using a SmoothStepper (well, you were in your previous posts), you may need to tell Mach that the spindle "direction" signal in "active low".  See our app note AN002 on page 5 of the PDF document (http://www.pmdx.com/AppNotes).  If you are running Mach4 then I'm not sure how to configure the spindle.

**HOWEVER** making the M3 command match the PMDX-107's test mode will run your spindle backwards.  So you should also check your VFD manual to see if there is a setting that controls how its "Direction" input works, if there is such a setting.  Or reverse the wiring as Steve suggested.  If you cannot change how your VFD interprets its direction input, then leave the the current Mach/Smoothstepper settings alone and just remember that the PMDX-107's test mode will run your spindle backwards.

Bob
Engineering Hell: Everything's right and nothing works.
Bob's Corollary: If everything's right and nothing works, double check your assumptions.