Author Topic: Fault at G320 after line count exceeded  (Read 4847 times)

kemlin

  • Posts: 17
    • View Profile
Fault at G320 after line count exceeded
« on: September 08, 2017, 11:50:01 AM »
I have been able to get my axis moving however they will only move enough to get the line count to go to the fault mode at the drive.  I am sure I have something in setup goofed up but wanted to run some things past you guys to see if I am missing the forest for the trees.  I have a PMD-126/107 going to Gecko G320X drives controlled by Mach III.  I have CUI encoders set to 500ppr and my lead screw requires 5 turns to make 1".  I set up in Mach to have 2500 pulses per unit.  The drives move accordingly so I am confident that I have the pin #s setup correctly for the servo output from Mach.  Do I need to run a "charge pump" to make things happy?  What am I missing?

Steve Stallings

  • Administrator
  • Posts: 530
  • www.PMDX.com/Images/Avatar120.jpg
    • View Profile
Re: Fault at G320 after line count exceeded
« Reply #1 on: October 01, 2017, 01:37:42 PM »
If your drives move the correct distance, then you have the counts
per unit configured correctly for your Encoder and G320 setup.

If the fault only occurs sometimes, you may have a tuning problem.
Try running with lower velocity. If this cures the problem, it is likely
a tuning problem.

The charge pump is required if you are using the PMDX-126 to
interface with the Err/RST terminal of the G320 drivers. If you are
manually resetting the drives and have not connection from the
Err/RST terminal to the PMDX-126, then a charge pump is not
required.

Steve Stallings
www.PMDX.com