Author Topic: Fault circuit PMDX-122  (Read 4743 times)

lgr

  • Posts: 8
    • View Profile
Fault circuit PMDX-122
« on: November 09, 2017, 02:23:18 PM »
I have a Mach3 driven FROGMILL with 2 of your 122 boards in series. One of the boards is set up for "e stop" the other "fault". I had a momentary short in the panel (not directly on the boards) and now I can't reset a fault on the mach computer screen. Both the estop and fault green LED's are illuminated, if i disconnect the fault wire nothing changes. Any suggestions? thanks

Steve Stallings

  • Administrator
  • Posts: 530
  • www.PMDX.com/Images/Avatar120.jpg
    • View Profile
Re: Fault circuit PMDX-122
« Reply #1 on: November 10, 2017, 04:56:17 PM »
There are many possible ways to utilize the e-stop and fault circuits, and even
more is you are ganging two cards. Without knowing the wiring and jumper
settings in you machine, it is difficult to offer usable advice.

The PMDX-122 will present E-Stop/Fault* status on pin 10 of the parallel
port as an active high signal.

The E-Stop input is activated when driven high, or when it is open circuit.
Normal operation requires the input to be connected to ground or driven
low.

The Fault* input is activated when the signal is driven low. If there is no wire
connected to the Fault/ terminal, the board will run normally. The E-Stop
input will override the Fault/ input, so you must ground the E-Stop input
if you want to be able to use the Fault* input by itself.

It is possible to daisy chain the fault logic between two boards, and use
the E-Stop input of the second board as a general purpose signal. To do
this see page 29 of the users manual here:

http://www.pmdx.com/Doc/PMDX-122_Manual_112.pdf

This shows the required interconnection and jumper settings.


Steve Stallings
www.PMDX.com